Unbalanced fault
I want to simulate one phase closed model for a specific line in PSS/E. I don't know about phase impedance value which is in per unit or ohm. I should enter that parameter in PSS/E. Can you help me? Thanks.
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
I want to simulate one phase closed model for a specific line in PSS/E. I don't know about phase impedance value which is in per unit or ohm. I should enter that parameter in PSS/E. Can you help me? Thanks.
Unbalanced fault in PSSE requires sequence data to be loaded. If Balanced or Unbalanced I would recommend ASCC. You can change the output settings in Misc>OPTN>Short Circuit. You can set Physical, PerUnit, Rectangular, Polar there.
Thanks to 3phaseee.com for help on this one.