Unbalanced fault
I want to simulate one phase closed model for a specific line in PSS/E. I don't know about phase impedance value which is in per unit or ohm. I should enter that parameter in PSS/E. Can you help me? Thanks.
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
I want to simulate one phase closed model for a specific line in PSS/E. I don't know about phase impedance value which is in per unit or ohm. I should enter that parameter in PSS/E. Can you help me? Thanks.
Unbalanced fault in PSSE requires sequence data to be loaded. If Balanced or Unbalanced I would recommend ASCC. You can change the output settings in Misc>OPTN>Short Circuit. You can set Physical, PerUnit, Rectangular, Polar there.
Thanks to 3phaseee.com for help on this one.
Asked: 2017-11-10 15:10:52 -0500
Seen: 1,354 times
Last updated: Nov 12 '17
Equivalent two-phase to ground fault admittances at Transmission nodes
unbalanced fault simulation in psse33
IEEE system bus data with sequence data for unbalanced fault
bus-3001 to bus-3003 unbalanced fault in official file 'savnw' cannot be added successfully.
Application of Unbalanced Faults in Positive Sequence Dynamic Simulation