Unbalanced fault

asked Nov 10 '17

Amir90 gravatar image

I want to simulate one phase closed model for a specific line in PSS/E. I don't know about phase impedance value which is in per unit or ohm. I should enter that parameter in PSS/E. Can you help me? Thanks.

1 answer

Sort by » oldest newest most voted
0

answered Nov 13 '17

knucklehead gravatar image

Unbalanced fault in PSSE requires sequence data to be loaded. If Balanced or Unbalanced I would recommend ASCC. You can change the output settings in Misc>OPTN>Short Circuit. You can set Physical, PerUnit, Rectangular, Polar there.

Thanks to 3phaseee.com for help on this one.

link