0

unbalanced fault simulation in psse33

Hi folks, when I do unbalanced fault simulation such as 1 phase fault and so on in PSSE ,It was failed to add fault,who can help me how to do it,thank you

psseboy's avatar
1
psseboy
asked 2019-12-23 02:23:59 -0500
edit flag offensive 0 remove flag close merge delete

Comments

Make sure you have sequence data.

sofostsant's avatar sofostsant (2019-12-26 22:10:32 -0500) edit

Your are right ! Because i a beginner so there not have the sequence data

psseboy's avatar psseboy (2020-01-03 00:51:58 -0500) edit
add a comment see more comments

2 Answers

0

hello I thanks that your simulation model is wrong (verify if you have the sequence data).

adnene's avatar
7
adnene
answered 2019-12-30 05:21:49 -0500
edit flag offensive 0 remove flag delete link

Comments

As shown in the figure,i don't have the sequence data

psseboy's avatar psseboy (2020-01-03 00:53:10 -0500) edit
add a comment see more comments
0

If you do not have any information on the sequence impedance, it would be impossible to determine.

If you do have the Thevenin sequence impedance at the particular bus you are applying a fault (and let's say not for anywhere else in the network), you can emulate a bolted single-phase fault by setting the impedance value to the sum of the negative and zero sequence components of the Thevenin impedance, and apply a three-phase fault.

likethevegetable's avatar
101
likethevegetable
answered 2020-01-24 14:02:49 -0500, updated 2020-01-24 14:03:38 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments

Your Answer