Switching in-service fixed shunt during a dynamic simulation

Hi all, I am a new user of PSSE. I would like to put in-service a fixed shunt during a dynamic simulation in the initialization is out-service. I really do not know the command which command to use. Can anyone give me a hand with the command? I have searched it but I still do not know. Thanks!

anonymous user
asked 2014-07-25 03:46:38 -0500
edit flag offensive 0 remove flag close merge delete

Comments

Hi PowerGuy it worked. Thanks! =)

GwenB's avatar GwenB (2014-07-30 00:24:57 -0500) edit
add a comment see more comments

2 Answers

1

From one of used files:

To add shunt

psspy.shunt_data(bus#,r""":""",1,[0.0,0.0])

psspy.shuntchng(bus#,r""":""",i,[_f, -267.0]) #comment -267 MVAR shunt.

To remove shunt

psspy.shuntchng(bus#,r""":""",0,[f,_f])

over and out.

Mahesh's avatar
113
Mahesh
answered 2014-07-28 00:38:21 -0500, updated 2014-07-28 00:39:14 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments
1

The Disturbance APIs section of the documentation doesn't give functionality for tripping or reconnecting shunts. I'd suggest you could move the shunt to a new bus, which is out of service, but connected to the original bus via a zero impedance line. During the dynamic simulation, you could use busdata2 to change the bus code to 1 (in-service) before using DISTBRANCHCLOSE to connect the bus (shunt and all).

Eli Pack's avatar
823
Eli Pack
answered 2014-07-28 00:44:27 -0500
edit flag offensive 0 remove flag delete link

Comments

The requested API is found in "Power Flow Data Changing" instead. It is just to use psspy.shunt_chng(i, id, 1) to switch on the shunt during the dynamic simulation.

perolofl's avatar perolofl (2016-09-29 14:52:56 -0500) edit