SVC and Induction Motors in the same bus

Can we install a SVC in a bus where we have induction motors as loads? This affects bus type (SVC will be switched off unless the load bus becomes a gen bus. Any idea on how to model this in PSSE. Thanks.

KM's avatar
1
KM
asked 2021-06-22 23:35:24 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

0

You can have an SVC modelled as a generator and induction motors as loads at the same bus. The bus type must be 2. It is ok to have loads at generator buses.

perolofl's avatar
3.8k
perolofl
answered 2021-06-23 03:23:47 -0500
edit flag offensive 0 remove flag delete link

Comments

Thank you. Appreciated