SVC and Induction Motors in the same bus

asked 2021-06-22 23:35:24 -0500

KM gravatar image

Can we install a SVC in a bus where we have induction motors as loads? This affects bus type (SVC will be switched off unless the load bus becomes a gen bus. Any idea on how to model this in PSSE. Thanks.

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2021-06-23 03:23:47 -0500

perolofl gravatar image

You can have an SVC modelled as a generator and induction motors as loads at the same bus. The bus type must be 2. It is ok to have loads at generator buses.

edit flag offensive delete link more

Comments

Thank you. Appreciated

KM gravatar imageKM ( 2021-06-23 05:46:38 -0500 )edit