Unbalanced fault
I want to simulate one phase closed model for a specific line in PSS/E. I don't know about phase impedance value which is in per unit or ohm. I should enter that parameter in PSS/E. Can you help me? Thanks.
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
I want to simulate one phase closed model for a specific line in PSS/E. I don't know about phase impedance value which is in per unit or ohm. I should enter that parameter in PSS/E. Can you help me? Thanks.
Unbalanced fault in PSSE requires sequence data to be loaded. If Balanced or Unbalanced I would recommend ASCC. You can change the output settings in Misc>OPTN>Short Circuit. You can set Physical, PerUnit, Rectangular, Polar there.
Thanks to 3phaseee.com for help on this one.
Asked: 2017-11-10 15:10:52 -0600
Seen: 1,361 times
Last updated: Nov 12 '17
Equivalent two-phase to ground fault admittances at Transmission nodes
unbalanced fault simulation in psse33
bus-3001 to bus-3003 unbalanced fault in official file 'savnw' cannot be added successfully.
IEEE system bus data with sequence data for unbalanced fault
Short circuit current as function of distance from bus
Simulation Crash at Fault Creation