0

Fault Analysis in PSSE

Hello. I have a project using PSSE. When I tried to do fault analysis I can't apply for L-G, L-L, and L-L-G. I only can apply the 3 phase fault. Is there any solution to solve this problem? Thank you

kemalmals's avatar
1
kemalmals
asked 2018-06-11 00:31:59 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

0

Sequence data (zero and negative) must be present in the save case in order to perform unbalanced faults.

perolofl's avatar
3.8k
perolofl
answered 2018-06-11 03:26:31 -0500
edit flag offensive 0 remove flag delete link

Comments

@perolofl how to get sequence data from .raw file

Gloria.Z's avatar Gloria.Z (2018-10-21 04:03:34 -0500) edit

Raw-file only contains positive sequence data. Sequence data are in a .seq file.

perolofl's avatar perolofl (2018-10-21 06:12:24 -0500) edit

Could you tell me how to get the sequence data? Thank you.

Gloria.Z's avatar Gloria.Z (2018-10-21 09:06:16 -0500) edit
add a comment see more comments

Your Answer

Login/Signup to Answer