Fault Analysis in PSSE
Hello. I have a project using PSSE. When I tried to do fault analysis I can't apply for L-G, L-L, and L-L-G. I only can apply the 3 phase fault. Is there any solution to solve this problem? Thank you
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
Hello. I have a project using PSSE. When I tried to do fault analysis I can't apply for L-G, L-L, and L-L-G. I only can apply the 3 phase fault. Is there any solution to solve this problem? Thank you
Sequence data (zero and negative) must be present in the save case in order to perform unbalanced faults.