Unbalanced fault (slg) in dynamic simulation

Hello, I am trying to do a dynamic analysis for transient stability and i have the following problem: I want to check the transient stability when an SLG Fault happens. I have added the sequence data but when i do a (R,X) = (0,0) the system always synchronises. When i change the (R,X) to a value different than 0 the system is desynchronised. Why does this happen and is there something i can do for it?

Thank you in response

sofostsant's avatar
1
sofostsant
asked 2020-05-25 06:12:46 -0500, updated 2020-05-25 06:58:28 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

0

If you have entered sequence data to the case, it is just to use disturbance "Calculate and apply unbalanced bus fault..."

perolofl's avatar
3.8k
perolofl
answered 2020-05-25 08:16:05 -0500
edit flag offensive 0 remove flag delete link

Comments

I use it and i am getting the results i describe in the question. Is it data problem or something else happens? I check the results from the angle plotting. When i enter 0 reactance and resistance it always synchronises after the fault. If enter an non-0 value after the fault it desynchronises

sofostsant's avatar sofostsant (2020-05-25 08:42:46 -0500) edit

OK, so you are talking about the impedance of the SLG fault. (0,0) is solid fault. Whenever non-zero values are used a fault impedance is used and the short circuit is less severe. It is strange that the system becomes less stable. What happens when it desynchronise? One generator out of step?

perolofl's avatar perolofl (2020-05-25 13:26:35 -0500) edit

The relative to the swing bus angle of the generator oscilates!! I find it quite odd because of that reason and i was wondering why that happens. The same thing happened in the savnw i got from jcondos drive. Is there a chance for my PSSE to malfunctioning? Or is it another problem?

sofostsant's avatar sofostsant (2020-05-26 01:22:47 -0500) edit

I don't understand what you mean. Of course there are oscillations in the rotor angles when you apply a short circuit.

perolofl's avatar perolofl (2020-05-26 02:55:09 -0500) edit

What i mean is when i apply an slg in dynamic sim the system after the oscillations always synchronises, but when i add zf even when i run the fault for 1 cycle it always desynchronises. Do you want me to give you the file to check the slg?

sofostsant's avatar sofostsant (2020-05-26 07:07:24 -0500) edit