Ask Your Question
0

Unbalanced fault (slg) in dynamic simulation

asked 2020-05-25 06:12:46 -0600

sofostsant gravatar image

updated 2020-05-25 06:58:28 -0600

Hello, I am trying to do a dynamic analysis for transient stability and i have the following problem: I want to check the transient stability when an SLG Fault happens. I have added the sequence data but when i do a (R,X) = (0,0) the system always synchronises. When i change the (R,X) to a value different than 0 the system is desynchronised. Why does this happen and is there something i can do for it?

Thank you in response

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2020-05-25 08:16:05 -0600

perolofl gravatar image

If you have entered sequence data to the case, it is just to use disturbance "Calculate and apply unbalanced bus fault..."

edit flag offensive delete link more

Comments

I use it and i am getting the results i describe in the question. Is it data problem or something else happens? I check the results from the angle plotting. When i enter 0 reactance and resistance it always synchronises after the fault. If enter an non-0 value after the fault it desynchronises

sofostsant gravatar imagesofostsant ( 2020-05-25 08:42:46 -0600 )edit

OK, so you are talking about the impedance of the SLG fault. (0,0) is solid fault. Whenever non-zero values are used a fault impedance is used and the short circuit is less severe. It is strange that the system becomes less stable. What happens when it desynchronise? One generator out of step?

perolofl gravatar imageperolofl ( 2020-05-25 13:26:35 -0600 )edit

The relative to the swing bus angle of the generator oscilates!! I find it quite odd because of that reason and i was wondering why that happens. The same thing happened in the savnw i got from jcondos drive. Is there a chance for my PSSE to malfunctioning? Or is it another problem?

sofostsant gravatar imagesofostsant ( 2020-05-26 01:22:47 -0600 )edit

I don't understand what you mean. Of course there are oscillations in the rotor angles when you apply a short circuit.

perolofl gravatar imageperolofl ( 2020-05-26 02:55:09 -0600 )edit

What i mean is when i apply an slg in dynamic sim the system after the oscillations always synchronises, but when i add zf even when i run the fault for 1 cycle it always desynchronises. Do you want me to give you the file to check the slg?

sofostsant gravatar imagesofostsant ( 2020-05-26 07:07:24 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

1 follower

Stats

Asked: 2020-05-25 06:12:46 -0600

Seen: 583 times

Last updated: May 25 '20