Ask Your Question
0

SVC trigger voltage

asked 2020-06-26 03:31:51 -0600

EM gravatar image

Hi,

How can I send voltage value to SVC in dynamic analysis. I want to monitor behavior on SVC during different voltage set point. Do anyone have some python script?

edit retag flag offensive close merge delete

2 answers

Sort by ยป oldest newest most voted
0

answered 2020-06-29 06:50:38 -0600

perolofl gravatar image

You don't write which dynamic model you are using!

Check the model data sheet for which VAR that is holding the voltage setpoint. Change that VAR during simulation and see if the model uses the new, updated value.

edit flag offensive delete link more

Comments

Hi, thanks for answering, I use ABBSVC1 model.

EM gravatar imageEM ( 2020-06-29 07:37:16 -0600 )edit

Change VAR(L+1)

perolofl gravatar imageperolofl ( 2020-06-29 07:44:45 -0600 )edit
0

answered 2020-06-26 13:42:13 -0600

jconto gravatar image

There is no need to 'send' voltage values to an SVC during a dynamic run, PSSe will do it. The SVC model is 'connecting' the SVC behavior to the system behavior. To monitor the voltage at the SVC bus (or remote controlled bus) and its Q output, add corresponding channels. Do independent runs for each voltage set point.

edit flag offensive delete link more

Comments

Thanks, but please can you give me some points how to do independent runs for each voltage set point. How to change voltage set point?

EM gravatar imageEM ( 2020-06-29 01:16:02 -0600 )edit