calculate power factor and the question of switched shunt

asked 2020-03-10 03:19:38 -0500

Crash gravatar image

Hello everyone,

I wondering know how to calculate power factor in PSS/E? and if there is a branch has line outage, may I adjust the switched shunt(capacitor/reactor) to solve this problem?

thank you!:))

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2020-03-20 15:08:00 -0500

Pasnos gravatar image

I am not sure I understand the question. Do you want to calculate some type of apparent power factor at some transmission line?

edit flag offensive delete link more

Comments

Yes! That's what I mean.

Crash gravatar imageCrash ( 2020-03-22 05:46:28 -0500 )edit

If you want to calculate the apparent power factor at some transmission line then you can simply extract the sending active and reactive power of the transmission line psspy.brnflo(FromBusNr,ToBusNr,ID and then just divide them

Pasnos gravatar imagePasnos ( 2020-03-24 17:43:58 -0500 )edit

OK, I extremely appreciate.:))

Crash gravatar imageCrash ( 2020-03-31 21:30:35 -0500 )edit