calculate power factor and the question of switched shunt

Hello everyone,

I wondering know how to calculate power factor in PSS/E? and if there is a branch has line outage, may I adjust the switched shunt(capacitor/reactor) to solve this problem?

thank you!:))

Crash's avatar
17
Crash
asked 2020-03-10 03:19:38 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

0

I am not sure I understand the question. Do you want to calculate some type of apparent power factor at some transmission line?

Pasnos's avatar
51
Pasnos
answered 2020-03-20 15:08:00 -0500
edit flag offensive 0 remove flag delete link

Comments

Yes! That's what I mean.

Crash's avatar Crash (2020-03-22 05:46:28 -0500) edit

If you want to calculate the apparent power factor at some transmission line then you can simply extract the sending active and reactive power of the transmission line psspy.brnflo(FromBusNr,ToBusNr,ID and then just divide them

Pasnos's avatar Pasnos (2020-03-24 17:43:58 -0500) edit

OK, I extremely appreciate.:))

Crash's avatar Crash (2020-03-31 21:30:35 -0500) edit
add a comment see more comments