Loadflow: Power factor in a remote bus

Hi,

In PSS/E v32, is there a way of using a machine to remotely control the power factor in a given bus?

I think that voltage can be controlled in this way, but it seems to me that PF can only be controlled locally.

Thanks

google's avatar
21
google
asked 2015-02-04 22:34:33 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

0

Basically, the machine is connected to a generator bus(PV). you have control over P and V.

In steady-state model, if you want to set the power factor at a bus, you can force the reactive power to +ve for lagging and -ve for leading according to the required power factor.

Another way is by changing the Scheduled voltage of the generator to get the desired power factor at the remote bus.

But in dynamics, you can operate a generator/plant in power factor control using the power plant controller(PPC) model.