some questions about power flow adjustment

Hello everyone

I want to carry out some experiments of power flow adjustment in PSS/E. 1)When I set the system power imbalance, the power flow solver can always make the system converge. However, in some cases, the power of the balancing machine will exceed the limit. I know that if the power of the balancing machine does not exceed the limit, the power flow of the system will not converge. However, I need this sick power flow scenario, because I hope to change this situation by switching capacitors /reactors. How can I avoid the balancing machine power out of limit by setting PSS/E. 2)Since I have not used capacitors/reactors in PSS/E before, I do not know the meaning of some of these parameters. For example, I don't know how to choose the control model and adjustment method. I don't know the meaning of binit, BLK Steps and BLK Bstep (Mvar).

I really need your help. Any idea or suggestion is OK. I would be very grateful, and I look forward to sharing these issues with you.

greatly's avatar
1
greatly
asked 2022-03-22 09:14:34 -0500, updated 2022-03-22 09:15:18 -0500
edit flag offensive 0 remove flag close merge delete

Comments

What do you mean with balancing machine? Swing bus?

perolofl's avatar perolofl (2022-03-23 09:08:15 -0500) edit
add a comment see more comments

1 Answer

0

Read about switched shunts in the manual! If you still don't understand how to use them, then you can use fixed shunts instead. They are straight forward to implement.

perolofl's avatar
3.8k
perolofl
answered 2022-03-23 09:07:35 -0500
edit flag offensive 0 remove flag delete link

Comments

Thank you very much. It is very useful.

greatly's avatar greatly (2022-03-23 10:12:19 -0500) edit