Calculating centre of inertia frequency, scaling?

asked 2018-03-15 09:35:04 -0500

anonymous user

Anonymous

Hey there,

I have code that acquires all frequencies and is used to find COI frequency to find ROCOF on COI frequency, so I can use the ROCOF to estimate system inertia when certain contingencies occur.

To make COI frequency, I need to scale the machines' frequency contribution. I do not understand what Mbase is. Is it equivalent to inertia constant or rated power? If not, how can I get these two values from PSSE? I've spent so long looking around.

Thank you for your time.

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2018-03-20 17:13:48 -0500

perolofl gravatar image

updated 2018-04-05 02:14:01 -0500

Mbase is the rated MVA power of the generator. The inertia constant H is found in the dynamic generator model.

edit flag offensive delete link more