Changing the Base Frequency in PSSE

I am simulating a system where Two different networks having 50 HZ and 60 Hz frequency which are connected via Back to Back HVDC. Since PSSE can take only One frequency at a Time. So I am converting the model of 60 Hz to 50 Hz.

I need to know which parameters would required to be changed in the steady state Load Flow Case as well as in Dynamic.? For Dynamic, the inertia constant of Machines and Motors will require an update. What is the relation of frequency with the inertia constant.? Thanks in advance.

Umair Bilal's avatar
1
Umair Bilal
asked 2021-07-31 07:45:26 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

0

There is no need to recalculate data since all data are in pu. See post ”How to simulate 2 systems with different frequency in one file?”.

Similarly, there is no need to update the inertia constant H!

So it is only needed to update the base frequency on the first row in the file with additional system data (network no 2).