SVC dynamic model

I am starting to model dynamics on SVC that has a power range +70 MVAr -200 MVAr.

What dynamic model should I use?

EM's avatar
55
EM
asked 2021-05-20 03:17:25 -0500
edit flag offensive 0 remove flag close merge delete

Comments

How is the SVC modelled in load flow?

perolofl's avatar perolofl (2021-05-20 05:24:07 -0500) edit
add a comment see more comments

3 Answers

1

I would recommend to model the SVC as a switched shunt or a FACTS in load flow and use a dynamic model from the library.

Modeling an SVC as a generator in PSSE was necessary 40 years ago, but is quite obsolete after introduction of switched shunts and FACTS in PSSE.

perolofl's avatar
3.8k
perolofl
answered 2024-01-15 06:54:21 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments
0

Choose CSVGN1 or 5 from generator model library. Set bus connected with SVC to type 2 set the generator Z-source value to bigger value ie 0+j999 puto insure your gen is not current source. Don not use Generator step up transformer.

gisosi's avatar
1
gisosi
answered 2024-01-12 09:03:23 -0500, updated 2024-01-12 09:07:14 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments
0

I would recommend one of the WECC SVSMO models.They are a better representation of actual equipment.
https://www.wecc.org/Reliability/WECC...

Alex P's avatar
46
Alex P
answered 2024-01-23 12:28:15 -0500, updated 2024-01-23 12:28:34 -0500
edit flag offensive 0 remove flag delete link