SVC dynamic model

asked May 20 '1

EM gravatar image

I am starting to model dynamics on SVC that has a power range +70 MVAr -200 MVAr.

What dynamic model should I use?

Comments

How is the SVC modelled in load flow?

perolofl gravatar imageperolofl (May 20 '1)

3 answers

Sort by » oldest newest most voted
1

answered Jan 15 '4

perolofl gravatar image

I would recommend to model the SVC as a switched shunt or a FACTS in load flow and use a dynamic model from the library.

Modeling an SVC as a generator in PSSE was necessary 40 years ago, but is quite obsolete after introduction of switched shunts and FACTS in PSSE.

link
0

answered Jan 23 '4

Alex P gravatar image

updated Jan 23 '4

I would recommend one of the WECC SVSMO models.They are a better representation of actual equipment.
https://www.wecc.org/Reliability/WECC...

link
0

answered Jan 12 '4

gisosi gravatar image

updated Jan 12 '4

Choose CSVGN1 or 5 from generator model library. Set bus connected with SVC to type 2 set the generator Z-source value to bigger value ie 0+j999 puto insure your gen is not current source. Don not use Generator step up transformer.

link