SVC dynamic model
I am starting to model dynamics on SVC that has a power range +70 MVAr -200 MVAr.
What dynamic model should I use?
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
I am starting to model dynamics on SVC that has a power range +70 MVAr -200 MVAr.
What dynamic model should I use?
I would recommend one of the WECC SVSMO models.They are a better representation of actual equipment.
https://www.wecc.org/Reliability/WECC...
Choose CSVGN1 or 5 from generator model library. Set bus connected with SVC to type 2 set the generator Z-source value to bigger value ie 0+j999 puto insure your gen is not current source. Don not use Generator step up transformer.