How does psse calculate frequency at bus?
I see that psse outputs the frequency at bus with BUSFREQUENCYCHANNEL. But how does it do the calculation?
Thanks
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
I see that psse outputs the frequency at bus with BUSFREQUENCYCHANNEL. But how does it do the calculation?
Thanks
Hello guys, thank you for your responses. So PSSE uses the derivative and washout filter for the bus calculations?
The Program Application Guide gives insight about the process of dynamic calculation but not about the method of frequency calculation at buses. Do you know where can I check this? Thanks
To complete the previous answer, I have also realized that pss/e uses a 3rd order median filter, after doing the derivative. the output of the median filter then goes to a low path filter, with time constant of Tf, defined as Dynamic solution parameter.
The bus frequency is calculated from the change in bus voltage angle. A filter is applied to smooth the frequency result, using a 0.04 s time constant for the filter. The frequency filter time can be changed in "Dynamic Solution Parameters".
Asked: 2018-11-05 17:29:16 -0500
Seen: 1,672 times
Last updated: Nov 09 '18