How does psse calculate frequency at bus?
I see that psse outputs the frequency at bus with BUSFREQUENCYCHANNEL. But how does it do the calculation?
Thanks
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
I see that psse outputs the frequency at bus with BUSFREQUENCYCHANNEL. But how does it do the calculation?
Thanks
Hello guys, thank you for your responses. So PSSE uses the derivative and washout filter for the bus calculations?
The Program Application Guide gives insight about the process of dynamic calculation but not about the method of frequency calculation at buses. Do you know where can I check this? Thanks
The bus frequency is calculated from the change in bus voltage angle. A filter is applied to smooth the frequency result, using a 0.04 s time constant for the filter. The frequency filter time can be changed in "Dynamic Solution Parameters".
To complete the previous answer, I have also realized that pss/e uses a 3rd order median filter, after doing the derivative. the output of the median filter then goes to a low path filter, with time constant of Tf, defined as Dynamic solution parameter.
Regarding documentation, section 25.3 "Model NETFRQ" of the Program Application Guide (V2) has a bit of detail about the frequency filter, but no more detail than the answers here.
Asked: 2018-11-05 17:29:16 -0500
Seen: 2,538 times
Last updated: May 11
Frequency change on load change in dynamic simulation.
Change the voltage reference in REGCA1 and REECA1 model during dynamic simulation
Bus net MW injection or extraction - Through flow
How to ramp the value of exciter output voltage in dynamic simulation?
Underfrequency Load Shedding Using a Frequency Gradient
Bus voltage recovery problem during dynamic simulation
whit loves you. Content on this site is licensed under a Creative Commons Attribution Share Alike 3.0 license.