1 phase opened fault in PSS/E
Hello, Can I simulate 1 phase opened fault in PSS/E? I mean just one side of a specific phase has been opened. Thanks.
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
Hello, Can I simulate 1 phase opened fault in PSS/E? I mean just one side of a specific phase has been opened. Thanks.
Yes, you can do that for branches without susceptance, i.e. B=0. First you have to take the branch out of service. Use SCMU - 2 phases closed - and enter the impedance of the branch, see picture below and POM 10.4.2.
Here I have first taken the existing branch between bus 3001 and 3003 in savnw.sav out of service.