Ask Your Question
0

1 phase opened fault in PSS/E

asked 2017-12-15 05:55:00 -0500

Amir90 gravatar image

Hello, Can I simulate 1 phase opened fault in PSS/E? I mean just one side of a specific phase has been opened. Thanks.

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2017-12-17 15:13:44 -0500

perolofl gravatar image

Yes, you can do that for branches without susceptance, i.e. B=0. First you have to take the branch out of service. Use SCMU - 2 phases closed - and enter the impedance of the branch, see picture below and POM 10.4.2.

Here I have first taken the existing branch between bus 3001 and 3003 in savnw.sav out of service.

image description

edit flag offensive delete link more

Comments

hi, can you tell me how to open this window?

AlexYang gravatar imageAlexYang ( 2018-04-24 03:02:31 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

Stats

Asked: 2017-12-15 05:55:00 -0500

Seen: 3,804 times

Last updated: Dec 17 '17