Ask Your Question
0

No participating dispatch buses in study system !?

asked 2017-05-03 06:19:24 -0500

MAJID gravatar image

updated 2017-05-04 04:21:50 -0500

Dear friends, i need your help please. When I run pv analysis i get this error : no participating dispatch busses in study system X. I've read all the related posts, but i still lost. I'm working on a mesh network ! And Maybe pv analysis work just in radial and simple network!?? And could you please explain to me how to use this : The subsystem busses code ?? The transfer dispatch method? Economic dispatch ?
Thanks in advance.

edit retag flag offensive close merge delete

2 answers

Sort by ยป oldest newest most voted
0

answered 2017-05-03 19:55:50 -0500

jconto gravatar image

PV analysis work on any type of network but there is no "Economic dispatch". Check the post "Some problem with PV analysis".

edit flag offensive delete link more

Comments

unfortunately,i've checked all the related posts. Have you any ideas about the difference between dispatch methods !

MAJID gravatar imageMAJID ( 2017-05-04 03:05:03 -0500 )edit
0

answered 2017-05-03 07:30:20 -0500

yaya gravatar image

plz can u check your mon file, are you sure of your sub file contain generation unit ?

edit flag offensive delete link more

Comments

In order to avoid complicate cas ,my subsystem source contain one generator bus and sink one non generator bus ,for mon file i don't think if there is a problem, on .mon file we chose juste voltage range and deviation

MAJID gravatar imageMAJID ( 2017-05-03 08:23:52 -0500 )edit

But the PV analysis is a transfer of generation between the source area and the sink area, so if there is no generation in the sink one, how he will dispatch the generation in this area? the is no plant to reduce

yaya gravatar imageyaya ( 2017-05-04 07:57:12 -0500 )edit

By reducing or increasing loads in the sink subsystem! Any way, I'm going to add generators into sink subsystem if that could resolve this issue

MAJID gravatar imageMAJID ( 2017-05-04 08:09:39 -0500 )edit

Dear friend @yaya , i've added generator in my sink subsystem ,but A new error replaces the old one it says : unable to increment transfer in the base case

MAJID gravatar imageMAJID ( 2017-05-04 08:32:09 -0500 )edit

if you want to reduce or increase loads, you can choose in transfer dispatch methods DFAX loads instead of DFAX generation

yaya gravatar imageyaya ( 2017-05-15 05:45:26 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

1 follower

Stats

Asked: 2017-05-03 06:19:24 -0500

Seen: 1,626 times

Last updated: May 04 '17