Ask Your Question
0

Having issues with initializing case in 33.4 version.

asked 2022-11-12 09:52:42 -0500

CynicalSuka gravatar image

My case built and initialized with no errors on work PC having version 33.9 shows multiple initialization errors on another PC having 33.4 version. Same case perfectly initializes on version 33.9. Some things that i dug up while trying to solve the issue. e.g if Vmax of some governor is correctly tuned in 33.9 version, that value shows initialization out limit error in 33.4 version. if Vmax=0.80 in 33.9 version i have to make it 0.83 or 0.84 in version 33.4 for this error to be removed. So, i have to do this tuning exercise again and again. Extremely annoying. Anyone else facing same issue?

edit retag flag offensive close merge delete

3 answers

Sort by ยป oldest newest most voted
0

answered 2022-11-16 14:17:18 -0500

Check with PSSE release notes. If there is no change in governor model then try checking your simulation/parameter setting and make sure those are same in both the versions.

edit flag offensive delete link more
0

answered 2022-11-12 09:53:47 -0500

CynicalSuka gravatar image

updated 2022-11-15 13:47:36 -0500

And this happens only for governor models. Would be glad if someone could help. i have to make TRATE of GGOV1 from 300 to 301 and then suspect error is removed. but case initializes with no error TRATE=300 in 33.9 version

edit flag offensive delete link more
0

answered 2022-11-12 14:26:19 -0500

perolofl gravatar image

Can you show load flow and dynamic data for a generator and the error messages?

edit flag offensive delete link more

Comments

Governor Data of one of the machine: Model Name Model Identifier Type R T1 (>0)(sec) V MAX V MIN T2 (sec) T3 (>0)(sec) Dt TGOV1 20100 [FPCL 132.00] 1 Stnd 0.0600 0.1000 0.8100 0.2600 2.1000 5.0000 0.0000

CynicalSuka gravatar imageCynicalSuka ( 2022-11-13 00:47:50 -0500 )edit

Load flow data of that machine: Bus Number BusName VSched (pu) PGen (MW) PMax (MW) PMin (MW) QGen (Mvar) QMax (Mvar) QMin (Mvar) Mbase (MVA) 20100 FPCL 132.00 0.9800 55.0002 55.0000 17.3330 37.1853 37.1850 -29.0590 68.75

CynicalSuka gravatar imageCynicalSuka ( 2022-11-13 00:49:32 -0500 )edit

it is clear that Vmax should be 0.80 or greater. i put 0.81 but still getting initialized out of limit error. i have to put 0.83 or greater for this error to be removed. this only happens in 33.4 version. in 33.9 it initializes without any error

CynicalSuka gravatar imageCynicalSuka ( 2022-11-13 00:50:55 -0500 )edit

The error: Model TGOV1 Bus 20100 [FPCL 132.00] Machine "1 " : initialized out of limit(s) PMECH(I)

CynicalSuka gravatar imageCynicalSuka ( 2022-11-13 00:51:28 -0500 )edit

Similar problems for other machines too.

CynicalSuka gravatar imageCynicalSuka ( 2022-11-13 01:03:56 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

1 follower

Stats

Asked: 2022-11-12 09:52:42 -0500

Seen: 499 times

Last updated: Nov 16 '22