0

Force generator P&Q limit in PSSE

Hi guys Can anyone tell me how to force P&Q limit in PSSE please. I want the PSSE not to go over the maximum P&Q limit in power flow or dynamic simulation.

Thanks in advance

KF's avatar
1
KF
asked 2019-12-04 20:40:38 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

2 Answers

0

For power flow studies, check out the GCAP function. In dynamic simulations, you have to build the logic into your AVR model.

jfconroy's avatar
186
jfconroy
answered 2019-12-05 01:26:41 -0500
edit flag offensive 0 remove flag delete link

Comments

Thanks jfconroy !

KF's avatar KF (2019-12-06 10:40:34 -0500) edit
add a comment see more comments
0

The maximum limit in the governor model (e.g. Pmax,gmax, etc) should be set to a value corresponding to the Pmax limit used in load flow.

perolofl's avatar
3.8k
perolofl
answered 2019-12-10 02:36:14 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments

Your Answer