Are the generator (power flow) limits also enforced in dynamic simulations?

Hi all,

In the psse raw file, within the generator data, there are limits PT and QT which (I believe) are for the power flow solution. However, i was wondering if these limits are also enforced during the dynamic simulations or not? My guess is a no. I think, the dynamic generation limits are enforced by the exciter and governor parameters (such as VMAX), which also depend on the generator MBASE.

Looking forward to your expert inputs on this

bikiran1991's avatar
47
bikiran1991
asked 2019-06-12 17:38:45 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

You are correct. The loadflow limits are not enforced in dynamic simulations.

perolofl's avatar
3.8k
perolofl
answered 2019-06-12 23:31:11 -0500