Ask Your Question
0

Are the generator (power flow) limits also enforced in dynamic simulations?

asked 2019-06-12 17:38:45 -0500

bikiran1991 gravatar image

Hi all,

In the psse raw file, within the generator data, there are limits PT and QT which (I believe) are for the power flow solution. However, i was wondering if these limits are also enforced during the dynamic simulations or not? My guess is a no. I think, the dynamic generation limits are enforced by the exciter and governor parameters (such as VMAX), which also depend on the generator MBASE.

Looking forward to your expert inputs on this

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
1

answered 2019-06-12 23:31:11 -0500

perolofl gravatar image

You are correct. The loadflow limits are not enforced in dynamic simulations.

edit flag offensive delete link more

Comments

thanks a lot!

bikiran1991 gravatar imagebikiran1991 ( 2019-06-13 10:46:03 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

1 follower

Stats

Asked: 2019-06-12 17:38:45 -0500

Seen: 861 times

Last updated: Jun 12 '19