How to simulate higher voltage
What is the best way to increase the voltage in the entire network to the limit values?
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
What is the best way to increase the voltage in the entire network to the limit values?
It would be good to know why you want an entire network in a high voltage state.
You can decrease the reactive consumption from loads (not a realistic scenario) or raised reactive injection (turn on capacitors or set generator voltage setting point to higher values).
Remember that voltage has a local impact so if you want to test a 'device' under high voltage condition, a localize high voltage condition can be created nearby such device instead of system wide HV conditions.
Asked: 2021-04-24 08:48:25 -0600
Seen: 181 times
Last updated: Apr 26 '21
HOW TO CALCULATE FVSI FROM DYNAMIC SIMULATION
Critical Clearing time calculation
Voltage calculation for nodes in a weighted undirected graph
How can you get the values of the sensitivity matrix?
Unbalanced fault (slg) in dynamic simulation
Pelec calculation based on Efd
unable to increment transfer in the base case!?
I want to suddenly change wind generator's reactive power during dynamic simulation. Please help.
How to do dynamic simulation to test the transient stability of power system?