Critical Clearing time calculation

For computing, critical clearing time for generating station in a grid network. I am applying bolted fault at generator bus in an iterative manner until the angle of the generator fails to reach its pre-fault value i.e. loses synchronism. The generator speed also reflects the same in the simulation. Any other factor to be considered for evaluation ? How does critical clearing angle comes into picture in this process ? It was also observed that even if generation in the nearest generators is varied in load flow. The ciritical clearing time still remains the same , Any observations in this regard ? Thanks in advance

Vikas07's avatar
1
Vikas07
asked 2020-09-09 07:31:09 -0500
edit flag offensive 0 remove flag close merge delete

Comments

Your question is not a PSS/E specific question, and you can find answers in any good textbook that covers power system dynamic stability, such as Kundur's "Power System Stability and Control".

jfconroy's avatar jfconroy (2020-09-09 08:40:19 -0500) edit

The query is , whether the above methology is correct to find critical clearing time in PSSE. How the critical clearing time is computed in PSSE ?

Vikas07's avatar Vikas07 (2020-09-09 09:05:49 -0500) edit
add a comment see more comments

1 Answer

0

Just supervise the rotor angle and check if the generator goes out of step, i.e., as you mentioned above.

perolofl's avatar
3.8k
perolofl
answered 2020-09-09 09:14:11 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments