CONTINGENCY MONITOR

asked Mar 25 '0

EM gravatar image

I have a problem with monitored voltage report in ACCC study.

I would like to see a voltage deviation on the bus during the N-1 analysis.

monitor file:

MONITOR BRANCHES IN AREA 8 END MONITOR VOLTAGE RANGE ALL BUSES 0.95 1.05 END END

TNX

1 answer

Sort by » oldest newest most voted
0

answered Mar 25 '0

jconto gravatar image

[from v.33, POM manual, section 8.1.3 Monitored Element Data File Contents] Add to the monitor file:

 MONITOR VOLTAGE DEVIATION ALL BUSES 0.05 0.05

where the last two parameters correspond to the magnitude of voltage drop in per unit and (last-item optional) magnitude of voltage rise in per unit.

link

Comments

Thanks, but again it is the same, I dont get any resaults.

EM gravatar imageEM (Mar 26 '0)

Erase all of the END in each line AND left just one at the end of the file.

Carlos G gravatar imageCarlos G (Mar 28 '0)

THANKS! It works now.