CONTINGENCY MONITOR

I have a problem with monitored voltage report in ACCC study.

I would like to see a voltage deviation on the bus during the N-1 analysis.

monitor file:

MONITOR BRANCHES IN AREA 8 END MONITOR VOLTAGE RANGE ALL BUSES 0.95 1.05 END END

TNX

EM's avatar
55
EM
asked 2020-03-25 06:36:32 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

0

[from v.33, POM manual, section 8.1.3 Monitored Element Data File Contents] Add to the monitor file:

 MONITOR VOLTAGE DEVIATION ALL BUSES 0.05 0.05

where the last two parameters correspond to the magnitude of voltage drop in per unit and (last-item optional) magnitude of voltage rise in per unit.

jconto's avatar
2.9k
jconto
answered 2020-03-25 16:08:35 -0500
edit flag offensive 0 remove flag delete link

Comments

Thanks, but again it is the same, I dont get any resaults.

EM's avatar EM (2020-03-26 07:17:46 -0500) edit

Erase all of the END in each line AND left just one at the end of the file.

Carlos G's avatar Carlos G (2020-03-28 00:35:07 -0500) edit

THANKS! It works now.

EM's avatar EM (2020-04-03 04:52:23 -0500) edit