CONTINGENCY MONITOR

asked 2020-03-25 06:36:32 -0600

EM gravatar image

I have a problem with monitored voltage report in ACCC study.

I would like to see a voltage deviation on the bus during the N-1 analysis.

monitor file:

MONITOR BRANCHES IN AREA 8 END MONITOR VOLTAGE RANGE ALL BUSES 0.95 1.05 END END

TNX

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2020-03-25 16:08:35 -0600

jconto gravatar image

[from v.33, POM manual, section 8.1.3 Monitored Element Data File Contents] Add to the monitor file:

 MONITOR VOLTAGE DEVIATION ALL BUSES 0.05 0.05

where the last two parameters correspond to the magnitude of voltage drop in per unit and (last-item optional) magnitude of voltage rise in per unit.

edit flag offensive delete link more

Comments

Thanks, but again it is the same, I dont get any resaults.

EM gravatar imageEM ( 2020-03-26 07:17:46 -0600 )edit

Erase all of the END in each line AND left just one at the end of the file.

Carlos G gravatar imageCarlos G ( 2020-03-28 00:35:07 -0600 )edit

THANKS! It works now.

EM gravatar imageEM ( 2020-04-03 04:52:23 -0600 )edit