0

CLOD model in PSS/E

Hello, I need default parameters of large motor and small motor in the CLOD model. Could you guide me? Thanks.

Amir90's avatar
1
Amir90
asked 2017-11-09 01:25:08 -0500
edit flag offensive 0 remove flag close merge delete

Comments

There are no default parameters, but I assume you mean typical parameters. It depends greatly on what system you are modelling, e.g. the amount of AC load or industrial load.

perolofl's avatar perolofl (2017-11-10 00:13:36 -0500) edit

The internal parameters of large motor and small motor aren't adjustable in the CLOD model so this model should have default parameters.

Amir90's avatar Amir90 (2017-11-10 07:07:00 -0500) edit

I thought you meant the percentage of small and large motors. See my answer regarding the motor parameters.

perolofl's avatar perolofl (2017-11-10 08:26:48 -0500) edit

Thanks a lot.

Amir90's avatar Amir90 (2017-11-10 14:56:37 -0500) edit
add a comment see more comments

1 Answer

0

The modelling of large and small motors in CLOD model is described in Program Application Guide, Volume II, Chapter 21.2.3 (rev 33).

perolofl's avatar
3.8k
perolofl
answered 2017-11-10 08:25:39 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments