how we make the choice of swing bus ?
When choosing the swing bus do we make the choice based on the machine that produces the biggest Pgen in the network or the machine with the highest value of inertia constant H ? Please help thnx in advance.
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
When choosing the swing bus do we make the choice based on the machine that produces the biggest Pgen in the network or the machine with the highest value of inertia constant H ? Please help thnx in advance.
The inertia constant has no effect in load flow calculation.
Normally you select a large generator as swing bus. However, any bus can be selected as swing, there is no need for a generator at the swing bus.
The most important is that the swing bus is electrically strong and is able to absorb any active power imbalance created when tripping generators, loads, HVDC lines, etc or after scaling total load/generation in the whole network or a subsystem.
A swing bus at high voltage level (e.g. 400 or 500 kV) is stronger than a swing bus at generator level (15-25 kV).
When performing voltage stability studies it is also good to locate the swing bus outside of the studied area, since the swing bus has no reactive power limits.
Asked: 2021-05-31 06:52:33 -0500
Seen: 1,859 times
Last updated: Jun 03 '21
I am having problems to find the write installation file for PSSE demo version
How to get current of bus and generator and use it in user defined model?
Can we edit outfiles created by PSSE using any other editor?
How to return machine CON description?
where and how can we generate dynamic data for the test systems in psse
PSSE34 Explore crashes all the time!!
Run multiple python files from one python file
What is the diffrence between REGCAU1 generator model and WT3G1 ?
whit loves you. Content on this site is licensed under a Creative Commons Attribution Share Alike 3.0 license.