Ask Your Question
0

how we make the choice of swing bus ?

asked 2021-05-31 06:52:33 -0500

anonymous user

Anonymous

When choosing the swing bus do we make the choice based on the machine that produces the biggest Pgen in the network or the machine with the highest value of inertia constant H ? Please help thnx in advance.

edit retag flag offensive close merge delete

1 answer

Sort by » oldest newest most voted
0

answered 2021-06-03 08:44:36 -0500

perolofl gravatar image

The inertia constant has no effect in load flow calculation.

Normally you select a large generator as swing bus. However, any bus can be selected as swing, there is no need for a generator at the swing bus.

The most important is that the swing bus is electrically strong and is able to absorb any active power imbalance created when tripping generators, loads, HVDC lines, etc or after scaling total load/generation in the whole network or a subsystem.

A swing bus at high voltage level (e.g. 400 or 500 kV) is stronger than a swing bus at generator level (15-25 kV).

When performing voltage stability studies it is also good to locate the swing bus outside of the studied area, since the swing bus has no reactive power limits.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

3 followers

Stats

Asked: 2021-05-31 06:52:33 -0500

Seen: 791 times

Last updated: Jun 03 '21