Ask Your Question
0

CLOD model in PSS/E

asked 2017-11-09 01:25:08 -0500

Amir90 gravatar image

Hello, I need default parameters of large motor and small motor in the CLOD model. Could you guide me? Thanks.

edit retag flag offensive close merge delete

Comments

There are no default parameters, but I assume you mean typical parameters. It depends greatly on what system you are modelling, e.g. the amount of AC load or industrial load.

perolofl gravatar imageperolofl ( 2017-11-10 00:13:36 -0500 )edit

The internal parameters of large motor and small motor aren't adjustable in the CLOD model so this model should have default parameters.

Amir90 gravatar imageAmir90 ( 2017-11-10 07:07:00 -0500 )edit

I thought you meant the percentage of small and large motors. See my answer regarding the motor parameters.

perolofl gravatar imageperolofl ( 2017-11-10 08:26:48 -0500 )edit

Thanks a lot.

Amir90 gravatar imageAmir90 ( 2017-11-10 14:56:37 -0500 )edit

1 answer

Sort by ยป oldest newest most voted
0

answered 2017-11-10 08:25:39 -0500

perolofl gravatar image

The modelling of large and small motors in CLOD model is described in Program Application Guide, Volume II, Chapter 21.2.3 (rev 33).

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

Stats

Asked: 2017-11-09 01:25:08 -0500

Seen: 861 times

Last updated: Nov 10 '17