First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!

Ask Your Question
0

CLOD model in PSS/E

asked Nov 9 '17

Amir90 gravatar image

Hello, I need default parameters of large motor and small motor in the CLOD model. Could you guide me? Thanks.

Comments

There are no default parameters, but I assume you mean typical parameters. It depends greatly on what system you are modelling, e.g. the amount of AC load or industrial load.

perolofl gravatar imageperolofl (Nov 10 '17)

The internal parameters of large motor and small motor aren't adjustable in the CLOD model so this model should have default parameters.

Amir90 gravatar imageAmir90 (Nov 10 '17)

I thought you meant the percentage of small and large motors. See my answer regarding the motor parameters.

perolofl gravatar imageperolofl (Nov 10 '17)

Thanks a lot.

Amir90 gravatar imageAmir90 (Nov 10 '17)

1 answer

Sort by » oldest newest most voted
0

answered Nov 10 '17

perolofl gravatar image

The modelling of large and small motors in CLOD model is described in Program Application Guide, Volume II, Chapter 21.2.3 (rev 33).

link