How to add a CMLDBLU2 or CMLDBLDGU2 with low power rating (<5MW)
I was working on the dynamic simulation of the IEEE 14 bus system with composite load models at all buses. The IEEE 14 bus test case has a load of 3.5MW on the 11th bus which is less than 5MW. While simulating this case I got a log report stating that "CMLDBLU2 At bus 11 LOAD 1 Ignored because real power= 3.5000 is less than threshold value of 5.00 MW". Is there any way to consider a composite load (CMLDBLU2/CMLDBLDGU2) with a power rating of less than 5MW? If yes, what changes are required to do that? Please help me to solve this situation.
Can you show the DYRE record?
I have added my dyre file in the answer as I cant add it here as a comment
What disturbance are you simulating?
the disturbance is a 100ms 3-phase fault at bus 13