Ask Your Question
0

Limits of PSSE Explore V34 and 35

asked 2023-09-18 16:02:10 -0600

AgustinMaroni gravatar image

updated 2023-09-18 16:02:42 -0600

I am trying to open a file ".sav" with less than 50 buses but the program fails to open it and send two alarms: "exceeds the dimensions of working memory" and "New size of case exceeds the size allowed by PSSE Xplore".

Which are the limits of PSSE Explore besides the numbers of buses?

edit retag flag offensive close merge delete

Comments

It's not only buses, but all other components such generators, loads, etc. are limited to different dimensions. If one of the limits is exceeded, such messages may come. You may try opening inbuilt cases such as savnw.sav to check.

chandv gravatar imagechandv ( 2023-09-18 23:02:58 -0600 )edit

1 answer

Sort by ยป oldest newest most voted
0

answered 2023-09-19 12:53:53 -0600

perolofl gravatar image

As @chandv wrote, open savnw network. The limits of the current version is shown with menu: "File - File information - List the number of system components".

For the 50 bus version:

  PTI INTERACTIVE POWER SYSTEM SIMULATOR--PSS(R)E Xplore TUE, SEP 19 2023  19:51
 PSS(R)E PROGRAM APPLICATION GUIDE EXAMPLE
 BASE CASE INCLUDING SEQUENCE DATA

             BUSES         PLANTS       MACHINES  WIND MACHINES  MACHINE OWNERS
 TOTAL          23              6              6              0             14
 MAXIMUM        50             15             20              5             40

                 S H U N T S                          INDUCTION
             FIXED       SWITCHED          LOADS       MACHINES
 TOTAL           5              0              8              0
 MAXIMUM        50             10            100             20

                        T R A N S F O R M E R S
          BRANCHES    TWO-WINDING  THREE-WINDING  ZERO IMPEDANCE  BRANCH OWNERS       MUTUALS
 TOTAL          34             11              0              0             35              6
 MAXIMUM       100             20              5             10            200             20

              MULTI-SECTION LINE
         GROUPINGS       SECTIONS          AREAS          ZONES         OWNERS      TRANSFERS
 TOTAL           2              4              3              4              7              4
 MAXIMUM         5             15             10             25             25             15


        2-TERM. DC     N-TERM. DC         VSC DC  FACTS DEVICES    GNE DEVICES     NCS TABLES
 TOTAL           0              0              0              0              0              0
 MAXIMUM         5              2              5              5              2              8

                                          SWITCHING DEVICES
       SUBSTATIONS          NODES      TERMINALS  IN SUBSTATION          TOTAL
 TOTAL           0              0              0              0              0
 MAXIMUM        16            200            200            200            200
edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

Stats

Asked: 2023-09-18 16:02:10 -0600

Seen: 521 times