How do you convert motor inertia into pu for PSS/e?

asked Feb 28 '3

LSilv gravatar image

PSS/e dynamic models require parameters to be in per unit. What's the formula to convert a motor's kgm2 inertia into per unit? Is it H = (0.5 * kgm2 * (motor RPM converted into rad/sec)^2)/motor MVA?

2 answers

Sort by » oldest newest most voted
0

answered Mar 2 '3

LSilv gravatar image

Right. Thanks.

link
0

answered Mar 1 '3

perolofl gravatar image

updated Mar 1 '3

It should be VA instead of MVA for the motor rating.