Ask Your Question
0

How do you convert motor inertia into pu for PSS/e?

asked 2023-02-28 11:33:08 -0500

LSilv gravatar image

PSS/e dynamic models require parameters to be in per unit. What's the formula to convert a motor's kgm2 inertia into per unit? Is it H = (0.5 * kgm2 * (motor RPM converted into rad/sec)^2)/motor MVA?

edit retag flag offensive close merge delete

2 answers

Sort by ยป oldest newest most voted
0

answered 2023-03-02 11:41:50 -0500

LSilv gravatar image

Right. Thanks.

edit flag offensive delete link more
0

answered 2023-03-01 08:16:17 -0500

perolofl gravatar image

updated 2023-03-01 08:19:45 -0500

It should be VA instead of MVA for the motor rating.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

1 follower

Stats

Asked: 2023-02-28 11:33:08 -0500

Seen: 456 times

Last updated: Mar 02 '23