0

How do you convert motor inertia into pu for PSS/e?

PSS/e dynamic models require parameters to be in per unit. What's the formula to convert a motor's kgm2 inertia into per unit? Is it H = (0.5 * kgm2 * (motor RPM converted into rad/sec)^2)/motor MVA?

LSilv's avatar
11
LSilv
asked 2023-02-28 11:33:08 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

2 Answers

0

Right. Thanks.

LSilv's avatar
11
LSilv
answered 2023-03-02 11:41:50 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments
0

It should be VA instead of MVA for the motor rating.

perolofl's avatar
3.8k
perolofl
answered 2023-03-01 08:16:17 -0500, updated 2023-03-01 08:19:45 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments

Your Answer