Is there any alternative function command for NSWICH in v35 ?

NSWICH command has been removed from common4.ins of v35. Is there any alternative function ? Please help me.

CPReddy's avatar
1
CPReddy
asked 2022-08-03 19:45:06 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

2 Answers

0

Switched shunts models are changed in rev 35 since multiple switched shunts are allowed at a bus.

The subroutine call is now SUBROUTINE XXXXXX(ISW,ISLOT), where ISW is the internal number of the switched shunt.

Since the switched shunt index (ISW) is an input into the model, any references to NSWICH (which was used to obtain the switched shunt index earlier) need to be removed.

See Chapter " Changes in Dynamics when Modeling Multiple Switched Shunts" in rev 35 Release Notes.

perolofl's avatar
3.8k
perolofl
answered 2022-08-05 03:43:40 -0500
edit flag offensive 0 remove flag delete link

Comments

Thanks for your suggestion.

CPReddy's avatar CPReddy (2022-10-28 13:43:30 -0500) edit
add a comment see more comments
0

Try

CALL SWSSEQ(IB, ID, 0, ISW)

IB is the bus sequence nmber (input) (Use BSSQNC to get this from the regular bus number).

ID is the shunt ID number (input)

ISW is the switch shunt sequence number (output)

PSS/E FORTRAN documentation is really underwhelming.

Alex P's avatar
46
Alex P
answered 2022-08-08 08:55:48 -0500
edit flag offensive 0 remove flag delete link

Comments

Hi Alex, Yes, now my code is working. Thanks for your support.

CPReddy's avatar CPReddy (2022-10-28 13:43:01 -0500) edit