Ask Your Question
0

How can I get Ipcmd and Iqcmd in REEC model.

asked 2021-09-28 05:15:28 -0500

penny870718 gravatar image

Hello everyone: I want to check the current limit logic in REEC model, so I want to check the Ipcmd and Iqcmd at the output of the REEC model, can someone tell me how to do it?

Sincerely, thanks.

edit retag flag offensive close merge delete

2 answers

Sort by ยป oldest newest most voted
0

answered 2022-05-02 09:37:05 -0500

CamelCamelCamel gravatar image

updated 2022-05-02 09:38:05 -0500

My 2 cents:

  • Open your case and dynamics in PSS/E
  • Dynamics (tab at top) -> List -> Model Storage Locations
  • Wind Machines -> Selected subsystem -> OK. This output will tell you where the storage locations are.
  • Now, from the Models.pdf, you can get the offsets of each channel from the base positions. A command to monitor that channel might look something like this:
  • BAT_STATE_CHANNEL, -1, 123456, 'Iq_MyGenerator'
edit flag offensive delete link more
0

answered 2021-09-30 01:09:58 -0500

Jorge gravatar image

Hi, You want to record VARs L+2 for the real current command (Ipcmd) and L+3 Reactive current command (Iqcmd) in your python script.

I hope that helps!

edit flag offensive delete link more

Comments

Oh, I see! Thanks for your advice, it's very useful!

penny870718 gravatar imagepenny870718 ( 2021-09-30 19:35:16 -0500 )edit