Can i calculate short-circuit ratio SCR using pss/e ?
hi currently i am working on a Ieee9 bus test case to perform short circuit analysis and i want to know if pss/e gives the value of SCR as an output
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
hi currently i am working on a Ieee9 bus test case to perform short circuit analysis and i want to know if pss/e gives the value of SCR as an output
The SCR is not calculated, but activity ASCC reports the short circuit power at the bus for three-phase faults. From that you can calculate SCR.
I have a question about short-circuit analysis can i plot short circuit current Icc? if yes how can i do that ? thnx.
Do you mean to plot the short circuit current in a dynamic simulation?
yes exactly can i do that ?
Split the faulted bus in saved case and add a MVA channel for the new ZIL between the buses. Calculate and plot the fault current with method 1 described in post "Monitor branch current in dynamic study".
thanks for your help
Asked: May 24 '1
Seen: 1,416 times
Last updated: May 25 '21
REGCAU1 model does not exist in pss/e how can i add this model to the library?
Short Circuit Bus Contribution
How i can make a push instruction to use in PSS
Short Circuit Current Use psse dynamic simulation and IEC module (psse34)
Short circuit calculation with type 4 wind turbines or PV generator
Hello can anyone help me about ANSI fault calculation ?
Short circuit equivalent generator
How can i simulate a wind farm using an aggregated model PSS/E ?
How to Convert synchronous generators into asynchronous generators?