A couple of questions on modelling short and equivalent generator for short circuit analysis. 1) How to derive the max short circuit MVA at a bus. 2) The Zth is available , but how to get X0/X1 ratio for representing zero and positive seq reactance in SC paramter of generator. Thanks in Advance

Vikas07's avatar
1
Vikas07
asked 2020-05-28 05:45:36 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

0

You should know at a minimum the system contribution to three-phase faults (magnitude and angle) and line-to-ground faults. With these, you can use what's in a power system analysis book to derive what you need. You also should consider transient and sub-transient responses and some way to optimize other model parameters to reflect that of the system you're modelling.