0

Can i calculate short-circuit ratio SCR using pss/e ?

hi currently i am working on a Ieee9 bus test case to perform short circuit analysis and i want to know if pss/e gives the value of SCR as an output

souha's avatar
13
souha
asked 2021-05-24 16:53:20 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

The SCR is not calculated, but activity ASCC reports the short circuit power at the bus for three-phase faults. From that you can calculate SCR.

perolofl's avatar
3.8k
perolofl
answered 2021-05-25 00:43:31 -0500
edit flag offensive 0 remove flag delete link

Comments

I have a question about short-circuit analysis can i plot short circuit current Icc? if yes how can i do that ? thnx.

Swej's avatar Swej (2021-05-25 05:57:15 -0500) edit

Do you mean to plot the short circuit current in a dynamic simulation?

perolofl's avatar perolofl (2021-05-25 07:01:06 -0500) edit

yes exactly can i do that ?

Swej's avatar Swej (2021-05-25 07:50:52 -0500) edit

Split the faulted bus in saved case and add a MVA channel for the new ZIL between the buses. Calculate and plot the fault current with method 1 described in post "Monitor branch current in dynamic study".

perolofl's avatar perolofl (2021-05-25 10:23:30 -0500) edit

thanks for your help

Swej's avatar Swej (2021-05-25 11:26:38 -0500) edit
add a comment see more comments

Your Answer

Login/Signup to Answer