Can i calculate short-circuit ratio SCR using pss/e ?

asked May 24 '1

souha gravatar image

hi currently i am working on a Ieee9 bus test case to perform short circuit analysis and i want to know if pss/e gives the value of SCR as an output

1 answer

Sort by » oldest newest most voted
1

answered May 25 '1

perolofl gravatar image

The SCR is not calculated, but activity ASCC reports the short circuit power at the bus for three-phase faults. From that you can calculate SCR.

link

Comments

I have a question about short-circuit analysis can i plot short circuit current Icc? if yes how can i do that ? thnx.

Swej gravatar imageSwej (May 25 '1)

Do you mean to plot the short circuit current in a dynamic simulation?

perolofl gravatar imageperolofl (May 25 '1)

yes exactly can i do that ?

Swej gravatar imageSwej (May 25 '1)

Split the faulted bus in saved case and add a MVA channel for the new ZIL between the buses. Calculate and plot the fault current with method 1 described in post "Monitor branch current in dynamic study".

perolofl gravatar imageperolofl (May 25 '1)

thanks for your help

Swej gravatar imageSwej (May 25 '1)