Can i calculate short-circuit ratio SCR using pss/e ?
hi currently i am working on a Ieee9 bus test case to perform short circuit analysis and i want to know if pss/e gives the value of SCR as an output
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
hi currently i am working on a Ieee9 bus test case to perform short circuit analysis and i want to know if pss/e gives the value of SCR as an output
The SCR is not calculated, but activity ASCC reports the short circuit power at the bus for three-phase faults. From that you can calculate SCR.
Asked: 2021-05-24 16:53:20 -0600
Seen: 1,319 times
Last updated: May 25 '21
REGCAU1 model does not exist in pss/e how can i add this model to the library?
How do I get the short circuit current with the ASCC_3 API?
How to Convert synchronous generators into asynchronous generators?
Short Circuit Current Use psse dynamic simulation and IEC module (psse34)
Hello can anyone help me about ANSI fault calculation ?
Short circuit equivalent generator
How i can make a push instruction to use in PSS
Short Circuit Bus Contribution
How can i simulate a wind farm using an aggregated model PSS/E ?