Can i calculate short-circuit ratio SCR using pss/e ?
hi currently i am working on a Ieee9 bus test case to perform short circuit analysis and i want to know if pss/e gives the value of SCR as an output
hi currently i am working on a Ieee9 bus test case to perform short circuit analysis and i want to know if pss/e gives the value of SCR as an output
The SCR is not calculated, but activity ASCC reports the short circuit power at the bus for three-phase faults. From that you can calculate SCR.
I have a question about short-circuit analysis can i plot short circuit current Icc? if yes how can i do that ? thnx.
Do you mean to plot the short circuit current in a dynamic simulation?
yes exactly can i do that ?
Split the faulted bus in saved case and add a MVA channel for the new ZIL between the buses. Calculate and plot the fault current with method 1 described in post "Monitor branch current in dynamic study".
thanks for your help