looking for a typical parameters of CMLDBLDGU2
I am looking for the parameters of a composite load such as "CMLDBLDGU2" in PSS/E. Can anybody help me how to find that? thank you.
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
I am looking for the parameters of a composite load such as "CMLDBLDGU2" in PSS/E. Can anybody help me how to find that? thank you.
@! CMLDBLDGU2.dyr - bus load CMLD + DG
@! WECC data, processed with NERC LMDT tool, formatted by jconto
4 'USRLOD' 1 'CMLDBLDGU2' 12 1 8 175 32 148 48
@! ICONs
0 0 1 0 0 1 1 1
@! CONS J, J+6
-1.0 0.0 0.04 0.04 0.08 1.0 1.0
@! CONS J+7, J+16
1.0 0.9 1.1 0.00625 1.025 1.04 30.0 5.0 0.0 0.0
@! CONS J+17, J+21
0.108850010868 0.114095056656 0.0605301020056 0.0860015181818 0.189206598581
@! CONS J+22, J+26
1.0 0.6 0.5 0.8 1.0
@! CONS J+27, J+36
2 0.647763667352 1 0.352236332648 0.0 2 1.0 1 0.0 -1.0
@! CONS J+37, J+56 - Motor A
0.75 0.104 0.059 0.04 1.8 0.12 0.095 0.0021 0.1 0.0 0.6 0.1 0.2 1.0 99999.0 0.45 0.02 0.75 0.6 0.1
@! CONS J+57, J+76 - Motor B
0.75 0.14 0.059 0.03 1.8 0.19 0.2 0.0026 0.5 2.0 0.5 0.02 0.3 0.6 0.05 0.45 0.025 0.3 0.55 0.05
@! CONS J+77, J+96 - Motor C
0.75 0.14 0.059 0.03 1.8 0.19 0.2 0.0026 0.1 2.0 0.53 0.03 0.2 0.63 0.05 0.48 0.03 0.3 0.58 0.1
@! CONS J+97, J+106 - Motor D
0.03 0.3 0.025 0.05 1.0 0.98 0.45 0.1 0.1 0.0
@! CONS J+107, J+114 - Motor D
0.0 1.0 6.0 2.0 12.0 3.2 11.0 2.5
@! CONS J+115, J+123 - Motor D
0.86 0.2 0.95 1.0 -3.3 0.5 0.4 0.6 0.5
@! CONS J+124, J+131 - Motor D
15.0 0.7 1.9 0.1 0.6 0.2 0.0 9999.0
@! CONS J+132, J+139 - DER
0.0 0.0 -0.1 0.1 1.0 0.0 0.025 0.02
@! CONS J+140, J+145 - DER
0.0 0.0 0.0 0.0 999.0 -999.0
@! CONS J+146, J+153 - DER
1.1 0.0 9.0 -9.0 0.1 0.1 0.05 1.2
@! CONS J+154, J+162 - DER
0.5 0.52 1.21 1.19 200.0 0.0 200.0 0.0 0.5
@! CONS J+163, J+174 - DER
59.0 61.0 1.0 1.0 0.02 5.0 0.2 0.8 0.5 -0.5 0.75 0.5 /Bus 4
Asked: May 3 '1
Seen: 295 times
Last updated: May 04 '21
How to plot alpha and gamma for the two-terminal DC line?
How can I change the Active power of Wind Turbine Generator WTG-Type 3 during dynamic Solution
DYRE Terminated--system model requires too many STAT
How to add dynamic data to an existing dynamic data in PSSE through Python?
Read variables during dynamic simulation
How to change Pgen of generators in dynamic simulation