SWTGU2 Time Step
It says "please set integration 7ms>= delt >=1ms"
Can this be fixed? Tia
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
It says "please set integration 7ms>= delt >=1ms"
Can this be fixed? Tia
The time step (DELT) is set in seconds in menu Dynamics - Solution parameters...
Change to a value between 0.001 - 0.007.
Asked: 2023-09-26 02:39:48 -0500
Seen: 303 times
Last updated: Sep 26 '23