Unbalanced fault (slg) in dynamic simulation

asked May 25 '0

sofostsant gravatar image

updated May 25 '0

Hello, I am trying to do a dynamic analysis for transient stability and i have the following problem: I want to check the transient stability when an SLG Fault happens. I have added the sequence data but when i do a (R,X) = (0,0) the system always synchronises. When i change the (R,X) to a value different than 0 the system is desynchronised. Why does this happen and is there something i can do for it?

Thank you in response

1 answer

Sort by » oldest newest most voted
0

answered May 25 '0

perolofl gravatar image

If you have entered sequence data to the case, it is just to use disturbance "Calculate and apply unbalanced bus fault..."

link

Comments

I use it and i am getting the results i describe in the question. Is it data problem or something else happens? I check the results from the angle plotting. When i enter 0 reactance and resistance it always synchronises after the fault. If enter an non-0 value after the fault it desynchronises

sofostsant gravatar imagesofostsant (May 25 '0)

OK, so you are talking about the impedance of the SLG fault. (0,0) is solid fault. Whenever non-zero values are used a fault impedance is used and the short circuit is less severe. It is strange that the system becomes less stable. What happens when it desynchronise? One generator out of step?

perolofl gravatar imageperolofl (May 25 '0)

The relative to the swing bus angle of the generator oscilates!! I find it quite odd because of that reason and i was wondering why that happens. The same thing happened in the savnw i got from jcondos drive. Is there a chance for my PSSE to malfunctioning? Or is it another problem?

sofostsant gravatar imagesofostsant (May 26 '0)

I don't understand what you mean. Of course there are oscillations in the rotor angles when you apply a short circuit.

perolofl gravatar imageperolofl (May 26 '0)

What i mean is when i apply an slg in dynamic sim the system after the oscillations always synchronises, but when i add zf even when i run the fault for 1 cycle it always desynchronises. Do you want me to give you the file to check the slg?

sofostsant gravatar imagesofostsant (May 26 '0)